Hi, as OPV use the value 38. This is the threshold between low load control and normal operation. While in normal mode SAT lets the boiler modulate freely, during low load control SAT sends the Max Modulation = 0% and calculates the ON/OFF times. Regarding the undershoot in the room temperature, you need to use a higher heating curve coefficient value. Try increasing in a step of 0.2. When the temperature in the room is stable on setpoint then you are done!

Replies: 1 comment

Comment options

You must be logged in to vote
0 replies
Answer selected by utarestev