SCT024 compatability and calibration question. #208
Unanswered
jsaintamour
asked this question in
Q&A
Replies: 3 comments 5 replies
-
You should have no problem using the 200A 0.33V CT's. You'll just need to cut the jumper on the back of the meter, which disables the on-board burden resistor. The voltage output CTs have their own burden resistor. After the jumper is cut, you'll be able to accurately calibrate the CTs. |
Beta Was this translation helpful? Give feedback.
2 replies
-
Ok i cut the jumpers on 5 and 6, and i am receiving higher amperage, but it still seems stuck around 9 amps. For reference CT2 and 5 are on the same load ![]() ![]() |
Beta Was this translation helpful? Give feedback.
3 replies
-
Beta Was this translation helpful? Give feedback.
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
-
I currently have 2 SCT016s connected to my meter and working wonderfully.
I recently ordered a couple SCT024s from aliexpress (only place i could find them) for monitoring my mains.
However i think i may have ordered the wrong ones.

I ordered 200a-0.333v, i think i needed the 200a-1v (which i may still order depending on how this goes).
My question is is there any way to calibrate the .333v to work with my meter?

Or do i need to bit the bullet and get the 200a-1v Here
currently when wired in, it only ever shows about 1 amp max (no matter how much i tweak the parameters in the config file).
Fore reference CT2 is a SCT016 calibrated, CT3 is on the same circuit and supposedly been calibrated using the function in the home assistant device page.