To start with positive and negative sequence admittance is modelled from the transformer rating in a pi model with each leg equal.

Simply put, zero sequence parameters are modelled equally as positive sequence parameters in transformers in pi model with extra conditions as follows:

  • The grounding admittance is added to zero sequence based on whether ground is available or not.
  • The admittances are added at respective ends only if the winding permits so. ie. there is a Yn or Zn connection. For rest the admittance is zero.
    Detailed explanation of a any branch's modelling is below. (Skip to zero sequence for your question.)

Link to Code: https://github.com/PowerGridModel/power-grid-model/blo…