EDIT: Ich habe gerade gesehen, du hast breits die notwendige Zeit-Intervalle vorgegeben am anderen Post 👍 Ich habe OpenDTU Version Firmwareversion / git Hash | 434ff8a laufen. Online / Offline Lüftermodus ist Automatisch |
Beta Was this translation helpful? Give feedback.
-
Only on my desk, sorry.
I can say for sure that "auto" causes the fan to slow down an ramp up depending on the load. I can't say that the temperature readings have much to do with its speed. To be honest, I don't think your fan is broken. If it runs fine at full speed and if that sounds like high RPM and if the sound is bearable, then it should be fine. If it does not sound like high RPM, then it might be stuck. If the sound is crazy loud, there is a physical issue (I had one of those fans in an older PSU, which I had to replace). |
Beta Was this translation helpful? Give feedback.
-
by the way, as per R4850G2 user manual(s), it seems as if 55 degrees C is the optimal temperature. V2.2 (EDIT: as identified by spcqike, the numbers in the graph are not percentages % , but Temperature: |
Beta Was this translation helpful? Give feedback.
-
Because the fan can be controlled via MQTT I just implemented the Node Red logic to switch from auto to full mode once either the temperature with the fan on auto exceeds 50°C or with full fan the temperature exceeds 35°C. Once full mode is activated a 5 minute counter counts down before it switched back to auto mode.
The input is a timestamp of 1 minute, output goes to a function which checks whether the state changed:
I'll report back in a few weeks to conclude whether this thermal control works and whether some modifications were necessary. Here's the JSON code
|
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
-
With the newest 2025.06.11 release I got curious on the fan control "full" and "automatic".

Something peculiar I discovered. On my R4850G2 the automatic fan control is not changing its fan speed as function of temperature!
I did a test, at 3kW permanently with fan control "auto" the temperature reached about 90°C. With "full" it went to 55°C, also at 3kW. Standing next to the setup with "auto" I didn't hear the fan rotating faster going from say 30°C to 90°C. At "full" it really roared.
To quantify that: "auto" about 28dB, at "full" about 45dB.
@schlimmchen you have a lot of experience with your Huawei right now. Does its fan increase its rpm's up (fully) towards 3kW and corresponding high temperatures?
I'm very positively surprised about the low 55°C at 3kW, because the high temperature at 3kW charging was always a concern for me. I opened a bug report, because that's probably more the appropriate location to catch people's attention.
Of course I researched a bit, I found this. Here also an Akkudoktor thread.
The Akkudoktor thread gives an indication that the fan might be broken, I just ordered a new one. Nevertheless it's weird that "full" works but "auto" not. Therefore I start here a discussion to find out whether other people have the same issue.
I remember quite some people have high temps at 3kW, with the 55°C at "full" speed it might be others also find out their fan isn't really ramping up when going from low charging speeds to 3kW....
Beta Was this translation helpful? Give feedback.