Replies: 1 comment 14 replies
-
Yes, the defrost cycle is completely normal and necessary. Go take a look at the outdoor unit’s fins just prior to defrost and it’ll be almost entirely covered in snow/frost/ice. The unit brings the hot liquid back to the condenser and melts this all away. What have you been noticing incorrect? |
Beta Was this translation helpful? Give feedback.
14 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
-
@Rev-777 I started a new discussion to avoid dragging the original away, but apologies I am slightly off topic for the whole forum here. I've bought one Faikin module to test but not screwed up the courage to install yet - I'm getting very close due to frustration with the temperature readouts from the built in sensors.
Our installation is a 5MXM90A2V1B9 with 3xFTXM25R2V1B, 1xFTXM20R2V1B and 1xFTXM60R2V1B
There is a second (possibly related) issue with frost/defrost cycles on the 5MXM at sub-zero temperatures. Frost builds up, and when it defrosts (up to hourly), heating is compromised for 15-20 minutes. Internal fans stop, the unit defrost takes 5 min (loads of water ejected) and then it takes 10-15 min to get back to full power. Have you noticed similar, since I see you are running in sub zero temp?
I fear a similar issue with the external unit thermistor, as I am able to see with the internal units. I will know more if I get around to installing the Faikin (and potentially voiding my warranty - at present I'm trying to get Daikin to fix it but I'm aware this may be a futile exercise and workaround may be all I have.)
Thanks in advance